Recipe in HMI vs PLC
Orn Jonsson
Apr 2002
Boise Idaho
125
Using AB ControlLogix and C-More touch screen.
My customer needs 50+ recipes each with 8 variables and 2 modifyers. They would like to use a Bar Code Scanner to load the recipes and a portion of the scanned bar code number to change the modifyers.
It seems that the HMI spreadsheet type recipe features require a user input for selecting a recipe. Therefore they would not work with a bar code scanner.
I was thinking about using a 2 dimentional array to hold the recipes and a Compare function to find and select the correct recipe row.
Any ideas on best practices with recipes are appreciated.
Orn,
I would write a UDT named recipe.
Each recipe would have a number say 1-50. When a product is scanned the relevant recipe will be loaded, and then could be checked to ensure the correct recipe has been loaded using a simple COMpare.
Mark
Orn,
I would write a UDT named recipe. (1)
Each recipe would have a number say 1-50. When a product is scanned the relevant recipe will be loaded (2), and then could be checked to ensure the correct recipe has been loaded using a simple COMpare.
Mark
I would not store the recipes on the HMI
(1) ...then make an Array tag to store your recipes : eg. Recipes[51]
(2) Use a LIM to check the scanned recipe number is 1-50, then simply copy the selected recipe to where you want it (add any other conditionals you might need, like sequence not running etc)
Hint : you can make use of array element 0 as the "Selected Recipe" (I usually do this with an Alias) - the code required for moving recipes around this way is very simple.
Selected_Recipe -> alias for Recipes[0]
LIM Recipe_Select, COP Recipes[Recipe_select] Selected_Recipe 1
If you aren't comitted to the C-More yet then consider using a RedLion G3. Since it has a programming language available its a lot more flexible. It can take your barcode input and it has plenty of user memory to store your recipes.
I've used both and I have to say I was less than enamored by the C-More. Without a programming language simple things require a lot of futzing around. The built in recipe objects in the C-More are a pain in the arse to use.
+1 to recipes in the HMI
+1 to Red Lion HMIs
I try to keep all programming in the PLC that I can. It causes the least amount of confusion.
I have done recipes on G3s and it is really the way to go if your PLC memory is limited. Recipes can take a large chunk of memory. Plus I find setting up the comms for a bar code scanner is easier on the G3 than a Control Logix if it is RS232 ASCII.
Hello, I'm working with an already developed system that uses enhanced recipe on the HMI. I'm looking for the control word to allow the PLC to...
4,849
Good afternoon, I need to create a recipes display on the hmi ns8, to change the parameters of a servo and some strings . The PLC that im using is...
2,772
I am working on trying to send and receive lists of BadgeIDs and User Access levels from a windows application to my system. My current theory is...
621
Hi there, I'm using a Siemens Simatic HMI. I have several screens where there are pull down menus to select a recipe. This was working fine for a...
2,271
Hey Guys, This one is driving me crazy. Has anyone ever encountered this before? I have a KTP400 HMI from siemens and i'm connected to a 315-2...
2,169