Red Lion G304K2 Comm issues
noxcuses
Jul 2010
North Carolina
29
I have a G304K2 connected to an Allen-Bradley L16ER Compactlogix processor. When the two are connected everything works as it should for several hours. Then the G3 will stop communicating and drops off the network. I've tried several new cables and have plugged the G3 directly into the PLC port with a short cable with the same results. The connection light on the switch doesn't change, so it has an ethernet hardware connection. The G3 doesn't reply to PINGS when this happens and the COM light flashes once every second.
To fix I cycle power on the G3 and everything goes back to normal for several hours. Any suggestions???
I am having the same issues with a G307K200 talking to a 1769-L30ER.
Sometimes it will work for hours before the comms drop out, but sometimes it will only last minutes.
GetDeviceStatus returns 101h when working but goes to 12h when it fails.
Restarting the HMI with CommitAndReset() gets it going again.
This is with 515.003 firmware and Native tags via L5k
This is something that we are working to resolve. In the meantime from our testing if you add a 100msec comms delay to each device it should fix the issue.
Jeremy
Hi all, I'm having programs connecting to a G304K2 over Ethernet to transfer the screens. I know on the older models, you first had to do a...
3,323
Hi all I am trying to upload a database to a brand new one of these, using latest crimson 3 software.. this is the first time i've used one of...
3,116
Hi guys, I have several Red Lion Kadet G304K and G304K2 terminals in service, and one particular client has now returned two of them with smashed...
2,950
Red Lion Crimson3.0 buttons G304K2 The background image changes, and I see that you can Move the text on press. Is there any way to have the text...
6,085
I have a Red Lion Cadet G304K2 HMI that I want to use to communicate with CompactLogix 1769-L30ERM using Ethernet/IP Is there a tutorial or...
12,394