REDLION G310 to Modicon 984-145
jnblackwood
Aug 2012
Oklahoma
PLC Info: Modicon AEG M//N: PC-A984-145 S/N: 20033182 Comp 984 CPU 8K MEM 1XMB MB+
HMI Info: REDLION Model G310 PT#: G310C210
Client's existing HMI device died and they bought a G310 to replace it. Needing to get the modbus communications up between the two without making changes to the PLC.
Probably a long-shot but has anyone done this before? Trying to go from the G310's RS232 port (RJ12 connector) to the Modicon's Port 1 (9-pin serial), and not sure how to configure communications in the Red Lion to get tag data.
Any help would be appreciated!
~James
~James
I've done a lot of Modbus, just not on a Modicon PLC, but the comms part is easy. Just add a Modbus Universal Master to the RS-232 port on the G310, set the drop number and you should be fine.
Start adding tags and map them to the appropriate registers.
The comms wiring is a different issue. I normally use the DRRJ11T6 DIN Rail adapter with the CBLRC02 to connect it to the Display. However, it looks like the CBLMOD01 is the direct connect cable.
That's actually what I did, but it still wasn't working so I thougt I had the wrong drivers or parameters.
However, it turns out they were using a bad cable. Once the cable was replaced it worked fine.
Hi All, I have a RedLion G310 panel which talks to a number of devices via Modbus. The G310 has both RS485 ports installed because one Modbus...
2,960
First Post here. I am an old hand with PLCs but new to the G3 and new to BacNet. I have a RedLion G310 HMI talking to a AB CompactLogix PLC. It...
2,297
Hi all I just upgraded our G306 to a bigger G310 display. The G310 just will not serve a web page to the Internet. I can see it on the LAN...
2,228
Has anyone found a good way to put electrical drawings on a G310? I tried the .pdf viewer, but it is painfully slow. It takes about 10 seconds...
2,424
I cannot make my MicroLogix 1400 and RedLion G310S210 communicate. The values all come up "---". I am using Crimson 3.0 software and using the...
7,791