redundancy in s7-400 using cpu 412-5H
ddhope
Nov 2012
india
how is redundancy accomplished using the above configuration? If the outputs are taken from both modules,wont they get added up?how does error detection take place?
hello.. I have already checked the system manual and the explanation is not clear enough to me.It has been explained with reference to digital output eg. to an HMI , i want to be clear as to how it works for analog outputs eg. to a valve.
If you read thoroughly you will see that one CPU is master and the other is (hot) standby. The master controls the outputs, dig. and ana., and the standby CPU gets updated process info via the h-link. If the master kneels, the changeover happens within 100ms.
Check tech info and the brochure. More pictures, less reading.
Kalle
Hi, I had a client upgraded their system to use a set of redundant PLC system with GE PLC CPE400, and a Citect 8.0 (2016) SCADA to get data with...
1,458
What is software redundancy, how to use, configure and test with plcsim ?????????????????????????????? In simatic Manager v5.4
2,693
Give me how to make redundancy in siemens s7 400, which we can check with plcsim...I didnt used redundancy till now....Basically iam a plc...
7,708
I am looking to understand how Siemens implements redundancy in their S7-400 series PLCs. Specifically, we provide a DCS that speaks modbusTCP...
4,231
All, I'm involved with a project using Siemens S7 400 CPUs. I want to build a redundancy two PLCs, actually I have no exprience about it. Anyone...
10,230