Redundant AB CLX with Modbus conversion

VicZA

Member
Join Date
Jun 2012
Location
Nelspruit
Posts
15
Hi Guys,

Maybe you have some experience with this set-up and can give me some pointers.

Project is to use an Emerson DCS to communicate (via MODBUS) with AB drives, E300, etc using a redundant system (communication channels A and B from the DCS).

We are looking using redundant CLX controllers to communicate with this setup. Is the only way to do this using a RED CLX pair with MVI modules in a 3rd rack? or could the MVI modules be placed in the two RED racks (as per attached picture).

Is there a better way to do this (maybe not using redundant PLCs) but guarantee two separate communication paths to the devices (channel A and Channel B)

Thanks
Vic

RED PLC 01.jpg
 
The recommended and supported method is to put the MVI modules into a remote chassis.

The ControlLogix redundancy manager modules can't manage I/O modules or specialty modules, only EtherNet/IP, ControlNet, and CPU modules.

Why are you using Modbus/TCP for this interface ? Emerson is notorious for being unhelpful in troubleshooting third party interfaces, but this sort of connection is exactly what the Mynah VIMs are for.

Is this a DeltaV or an Ovation or something else ? Why do you think that you need separate communication paths ?
 
The DSC is Ovation.

It has been designed that way, having two independent paths, A and B ... allowing for redundancy. If path A fails (for whatever reason) then path B takes over ... that's how it has been explained.
 
You can only put Processor, EN2T, CN2 and RM2 in redundancy chassis.
Any other modules will cause system disqualification.

Modbus must go into remote chassis
 

Similar Topics

Hi everybody, I have a CLX system with 2 redundant 1756-L71. Our customer requires two values: "CPU1_OK" and "CPU2_OK" to be sent via modbus...
Replies
0
Views
1,194
AB Gurus, I have a problem with RSLinx auto configuring nodes on the wrong driver. I have dual ethernet (2 ethernet networks completely separate...
Replies
2
Views
5,674
Hi guys, I'm sizing up a redundant CLX setup using 1757-SRM modules. 2 CPU, 2 SRM modules, 2 racks, 2 p/s. But I'm not sure if I should buy...
Replies
3
Views
2,533
I would like to set up a redudnat CLX processor configuration using the redundancy module. I would like to integrate this system into an existing...
Replies
4
Views
2,909
Hi, Does anyone know if we can put a Prosoft Modbus module in the ControlLogix redundant CPU Chassis each? Will it cause any negative effect to...
Replies
2
Views
3,361
Back
Top Bottom