So, we have a dual redundant PLC5/40 system using BCM and BEM Modules. 1CH of RIO and 2 of DH+. The DH+ are to be removed and migrated to Ethernet.

The PLC's are not to upgraded as of yet, but management want to replace with PLC5 Ethernet processors. Im not sure (cant see in manuals etc) if Ethernet processors work with BCM.

Ive experience of Control Logix redundancy, and understand that the RM adds +1 to the IP address, but i guess the BCM Module cant talk across the PLC 5 backplane to do the same???
 
I have not worked with PLC5 redundancy for a while, but I do recall that the BCM and BEM modules are built for RIO and DH+ switching.

PLC-5E controllers can be used, but the Ethernet channel will not be managed or affected by the redundancy modules. HMI and controller to controller message retargeting would have to be done manually.
 
Only the old Controlnet PLC5s had a truer form of redundancy than those BCM modules which didn't really give you true redundacy.
 

Similar Topics

I have been trying to find out if there are any redundant ethernet possibilities with a single PLC and 2 ethernet connections. The idea is that...
Replies
8
Views
3,230
Hi guys, Just wondering if anyone has tackled an issue similar to this before: creating a redundant master on Modbus so I can have a redundant...
Replies
2
Views
462
Good morning to all, I need to modify PLC configuration adding a new Profibus card. I've an issue during upload of actual configuration. With my...
Replies
1
Views
612
Hi sir. We are using Control logix redundant PLC system which supports only PTP time synchronization protocol but from DCS side we are receiving...
Replies
1
Views
2,447
Dears ALL I am preparing new PLC panel I want from the contractor to make redundant CPU , power supply and I/O modules, the contractor refuse to...
Replies
10
Views
3,109
Back
Top Bottom