Renu hmi with ml1500

advmin

Member
Join Date
Mar 2023
Location
Sheffield
Posts
59
Hi all,

PLC : Micrologix 1500 lrp
HMI : Renu FP3070 TN

I am a beginner in the plc world.
I am trying to connect the renu hmi with ML1500 lrp in channel 1 with RS 232 cable.
The software for Renu hmi is Flexisoft.

How can I establish the communication between the HMI and the plc so that I can energize input through it?

In the rslogix, I had configured channel 1 as 9600 baud rate and df1 full duplex.

In the HMI software, selected ML1500 and configured the same baud rate.

Could anyone please guide me on how to connect a different hmi with ML 1500?

cheers
 
No, I have connected the HMI with the Plc channel 1 port through Rs 232
How to find out whether they are communicating or not?
I checked the rslinx but was unable to get a lead due to unfamiliarity with this setup
 
I am not familiar with that HMI but I would recommend that you use its programming software to create a tag addressing the PLC and use it on a display page, download it and see what you get.

If you use the address S:4 you should see a rapidly changing number. That is the system free running clock that increments every scan.
 
Thanks, guys for your replies.
The issue was with the baud rate configured in channel 1.
After setting it to 9600, everything works fine.

I would recommend that you use its programming software to create a tag addressing the PLC and use it on a display page

Now the communication is working fine. Thanks for your suggestion OkiePC and DarryIR


cheers
 

Similar Topics

I have a RENU ELECTRONICS make HMI Model no. FP5121TN & I have to coonnect it with ABB make PLC AC500 how could it possible?
Replies
0
Views
1,388
I would like to know the node settings / communication settings and tag address defining for establishing a communication between micrologix 1200...
Replies
2
Views
2,873
Has anyone used a Prizm 230 HMI or other HMI's from Renu? I have an application with limited panel space - 3 inches tall max. I downloaded the...
Replies
1
Views
3,624
Hello all, Inverter/VFD : MITSUBISHI FR-D740-036-EC (3 phase,400V) PLC: RENU FL0050808402U I am trying to connect the RENU plc with the inverter...
Replies
10
Views
1,151
I am using Factory Talk view Machine Edition Runtime HMI. I want to configure on button in such way that when i press this button I want to...
Replies
3
Views
117
Back
Top Bottom