I have 1 rack PLC with prosoft modbus serial RS-485 (MVI56-MCM) installed on one of the slot on the rack. it configures as master with 2 slaves.
Currently this module is faulty and i have to replace it with new one. Do we need to upload the existing configuration file with prosoft builder software then load it to the new one or we can just plug it and play? please advise.
i am more familiar with Modbus Ethernet (MVI56-MNET) which required upload the existing config file then load it to the new one.
Thank You,
Muterdewe
In my experience, the classic MVI56-MCM module receives all of its configuration via the ControlLogix relay ladder program. Prosoft Configuration Builder is not used with the MVI56-MCM.
The "enhanced" MVI56E-MCM might use Prosoft Configuration Builder, but I'm confident the old ones did not.
Hi Ken,
thank you for your prompt response. are you saying that the MVI56-MCM can be plugged and play online without futher configuration?
regards,
Muterdewe
Check the configuration jumpers carefully on the module you remove. The physical configuration of the ports (RS-232, RS-422, RS-485) is done via those configuration jumpers.
But otherwise if the sample code was followed correctly, the PLC program should re-load the configuration blocks automatically.
Ken is correct. The ONLY thing you need to do is change the jumpers to match what your current module is set for, and plug it in. All configuration will come from ladder. This is true for both MVI56-MCM and MVI56E-MCM.
We have a Beckhoff CP6201 PC and an EK1100 module communicating with it via EtherCAT in one of our machines. Due to problems with the PC, I want...
81
Panelview 2711-K5A8. Customer has 6 of these in service connected to SLC 504’s. One has a bad backlight and I need a solution to replace it...
2,278
I’ve got some devices that are triggered by shorting pins to common. There is 24 volts on each pin and right now I am using a relay output card...
2,620
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
1,523
How can I achieve the same functionality in Studio 5000? Image 001.png for the old RSLogix500 program Image 002.png for conversion to Studio...
2,570