Residual current breaker trips with frequency inverter.
Karsten
Feb 2006
Odense
158
I have a problem with a "mobile" equipment with a frequency inverter. The equipment trips the residual current breaker. I have bee reading a little. By disconnecting the EMC filter it seems to work but I do really not want to do that.
Ideas??
It's normal since the filter leak to ground. If you disconnect the filter you will introduce interference on the line.
I had issues with 2 VFD's (two different brands) tripping a 30mA RCD. Moving to a higher mA RCD wasn't an option so it was cured by adding an isolation transformer.
It was portable equipment, so, between the 3 pin socket and equipment 3 pin plug. Looked like a "tradie's" 110V transformer for site work, only it was 230->230V not step down. Like this only 3KVA.
There are RCDs which can solve problem . When it comes to Eaton (ex Moeller) and Schrack products they have -U at the end of product type name.
If an isolation transformer is downstream of an RCD, then
anything downstream of the transformer is no longer RCD protected. You would have to put in another RCD downstream of the isolation transformer if the situation needs RCD protection.
I would like an opinion from pannel builders if you use or not Residual current protective devices in your control pannels. Thanks
5,970
Hello to all, can you please provide an example of obtaining a current working directory as a string in CodeSys? For example, during starting the...
230
Today I was working on my project for school and we were using a power supply with 24V and we accidentally had the current at 0.9A. We heard a pop...
588
Hi all, I have been working on a project that requires me to measure the current across a 90 VDC motor of a medical device (similar to an...
26
1,744
HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
718