So, I have either interesting or stupid problem.
We have ERIO network which we would like to be in a ring topology. Our ring master would be M580 eH58 4040 (hot standby) PLC, which is actually two PLCs (A and B), where one is a STAND-BY PLC while other is in RUN.
ERIOs are now powered and everything is visible on a network. When we close the ring interesting thing happens - our network starts to flicker. What I mean is that every 10 to 20 seconds network goes down for a 1-2 seconds approximately, visible online with PLC and red lights also appears on PLC and Ethernet RIO heads.
When we make a break and make a network linear we have no issues, everything runs smoothly.
I'm sure hardware is properly configured, CPU is a root on RSTP while CRA 312 00 are defined as participants.
We have NRP 312 00 fiber optics converters which we use to to enable fiber optics ring configuration.
I'm curious about what do you think could be a reason that fiber optical ring network doesn't work? If RSTP is configured properly then there should be no problems. NRP cards all have correct light indications showing communication exists (R and T ports seem to be matched correctly). I've noticed that FX light goes continuously green when this problem happens, usually it flickers, don't know if it indicates something.
Any idea where to look for a problem is appreciated, especially that nobody here has much experience with Modicon PLCs.
We have ERIO network which we would like to be in a ring topology. Our ring master would be M580 eH58 4040 (hot standby) PLC, which is actually two PLCs (A and B), where one is a STAND-BY PLC while other is in RUN.
ERIOs are now powered and everything is visible on a network. When we close the ring interesting thing happens - our network starts to flicker. What I mean is that every 10 to 20 seconds network goes down for a 1-2 seconds approximately, visible online with PLC and red lights also appears on PLC and Ethernet RIO heads.
When we make a break and make a network linear we have no issues, everything runs smoothly.
I'm sure hardware is properly configured, CPU is a root on RSTP while CRA 312 00 are defined as participants.
We have NRP 312 00 fiber optics converters which we use to to enable fiber optics ring configuration.
I'm curious about what do you think could be a reason that fiber optical ring network doesn't work? If RSTP is configured properly then there should be no problems. NRP cards all have correct light indications showing communication exists (R and T ports seem to be matched correctly). I've noticed that FX light goes continuously green when this problem happens, usually it flickers, don't know if it indicates something.
Any idea where to look for a problem is appreciated, especially that nobody here has much experience with Modicon PLCs.