I am in the middle of a project which needs me to use remote IO which I have never setup before.I have read the user pdf files for the scanner and the adaptor modules and think I have got it sussed.Just thought Id check before diving in.The scanner card is in slot 9 of my rack ,I have two remote 4 slot racks each containing a 1746 IB16, a 1746OW8 and 1746 NI4. I decided to use 1/2 slot addressing as image space isnt an issue and the client wants the code to be a simple as possible so i dont need to do any block transfers.Anyway I think the addressing should be as follows
Addressing Rack 1
Input card: - I: 9.0/00 – I: 9.0/15
Output card: O: 9.2/0 – O: 9.2/7
Analogue Card: - I: 9.4 channel 0, I: 9.5 channel 1, I: 9.6 channel 2, I: 9.7 channel 3,
Addressing Rack 2
Input card: - I: 9.8/00 – I: 9.8/15
Output card: O: 9.10/0 – O: 9.10/7
Analogue Card: - I: 9.12 channel 0, I: 9.13 channel 1, I: 9.14 channel 2, I: 9.15 channel 3,
Is this correct?
Addressing Rack 1
Input card: - I: 9.0/00 – I: 9.0/15
Output card: O: 9.2/0 – O: 9.2/7
Analogue Card: - I: 9.4 channel 0, I: 9.5 channel 1, I: 9.6 channel 2, I: 9.7 channel 3,
Addressing Rack 2
Input card: - I: 9.8/00 – I: 9.8/15
Output card: O: 9.10/0 – O: 9.10/7
Analogue Card: - I: 9.12 channel 0, I: 9.13 channel 1, I: 9.14 channel 2, I: 9.15 channel 3,
Is this correct?