RIO status on Panel View
bornwild
May 2010
Riyadh
429
Dear All,
I have compact logix controller with a couple of RIO over ethernet 1734 aentr. I would like get the Ethernet link status between all and place the status in the panel view for the hmi. Incase the rj45 connector goes loose. What is the bit to use to be used
Create a INT Data Type tag and place it within the Destination of a GSV instruction configured as:
Class name = Module;
Instance name = 'the monitored Point IO EIP adapter name';
Attribute Name = "EntryStatus".
Bit 14 of the INT tag (the Destination of the GSV instruction) will reflect the 1734-AENTR connection state: ON for connected and OFF for disconnected.
Recently we've had some faults and disconnects with our 1734 aent/r module. It shuts down all processes associated with the remote IO, obviously...