RMC100 analogs & decel distance
You should try ramping the pressure instead of making step changes. In the first plot you can see that when you reduce the pressure set point in one step at, 7.8125 s, it reduces the control output by a step too. You must be able to hear or even feel this.
Here in plot ram100 I put in a 1 second ramp for the pressure and helped it a lot. I still see some dip from it but not too bad. I think I'll stop for now until I get some material to press on.
As always you have given me a better understanding. Thanks for the help.
Better but
I would wait to decrease the pressure and now that the press limit is lower whey the press makes constact the pressure is overshooting.
Why have the pressure set to 2000 in the first place?
You should now consider slowing the press down just before you make contact. That will reduce the kinetic energy that causes the pressure spikes. Reducing the speed by half reduces the energy and resulting pressure spike by a factor of 4. Even a small slowdown can help a lot.
You must be closing on something very hard because the pressure is increasing very rapidly. More derivative gain on the p/F PID will help reduce the overshoot.
Im just pressing on steel plates so its very hard. Im going to look for something else better tomorrow but the customer will have material to me on Tuesday. I don't want to put a lot of work into something and then redo all of it on Tuesday.
If something happens on the fast move down I want to limit the amount of pressure. For example, the operator forgets his wrench in the machine. Unfortunately I have had this type of problem.
I just ran accross a little problem when trying to send a -10000 from WinAC RTX to a RMC100 motion control. When the number gets less than -1255...
2,669
I am trying to setup an RMC100 motion controller to communicate via EthernetIP with a control logix processor. I have followed the instructions...
7,623
I have read the Rmc100 manuals and i am still not too sure on how to redirect command and status registers on my plc (cs1h-h cpu 65). I will be...
3,047
Hi. Which of these system bits should I use to know that a particular AI or AO channel is faulted? Like I lost the 4-20mA loop, or the input is...
882
I have PanelView Plus 600 with the card slot that supports 1784-SDx and 1784-SDHCx SD cards. What're any compatible analogs?
2,277