Hi
I have a couple of hmi panel view plus 700
Hmi and we keep dropping coms /stars in the data boxes
I’ve checked the plc and unmanaged switch and can’t see an issue , if we reboot the power then it starts ok ?
Is there any way I can capture this fault?
 
is the PLC and all HMIs at the same subnet and connecting to one unmanaged switch? if that is the case, i would replace unmanaged switch to try.
 
Last edited:
It may be that your data boxes are not big enough for the data.
if it is an integer or real number, is the data box on the panelview set up for a negative number?
is the data box set up for a larger number than you thought possible?
james
 
Thanks for the reply’s.
This is only a intermittent issue it does normally work ok until the we have a drop of communication
And the only way I can get it to reboot is turning the power off and on ?
Don’t know how to capture the cause of this issue
 
Check the comm settings of the HMIs and the PLCs. If they don't match or are not set to auto-negotiate, it may cause some connectivity but tends to be flakey. I had this issue with a PLC where it would stop communicating after so much time elapsed due to mis-matched settings. We'd have to power cycle the machine then it would start working again. Check the communication section of your PLC for FCS errors or packet collisions.
 
If you are seeing question marks, then it is a loss of communications. If you are seeing asterisks (stars) that means the data is too large to be displayed. For example the object is formatted for two characters but the number is 100 or larger. That would require three characters, so it would be too large to be displayed. You would then see two asterisks ** instead of a value. If you had lost communications you would see two question marks ??

OG
 

Similar Topics

I want to program an Exor HMI using a Rockwell controller. However, when exporting the tag list from the controller and importing it into JMobile...
Replies
0
Views
125
Hi All, I am taking a deep dive into my facilities HMI Thin Manager Server which has been alarming for High CPU usage. We are using FactoryTalk...
Replies
2
Views
125
Hello everybody I work for an organization that treats wastewater. We are in the process of migrating 200 pumping stations to another...
Replies
0
Views
838
I have a PanelView hmi stuck at the boot screen. How can I make it run again? Allen-Bradley 2711-T10C15L1 PanelView 10.1" Touch Screen Terminal
Replies
2
Views
2,484
Hi Experts! I am trying to get a Redlion Crimson 3.0 HMI to talk to a Rockwell Emulator. I imagine I'll have to use OPC DA. Has anyone done this...
Replies
0
Views
1,180
Back
Top Bottom