I was wondering if anyone can help me. I am trying to setup a kinetix 350 drive with a compactlogix L36.
The problem I am having is that as soon as I assign the drive to a motion group, it faults with "FC06" and then reboots. When I click on the axis (ie: X_AXIS) the conditions are as follows:
Axis State: Faulted
Axis Fault: ConfigFault
Module Faults: ModuleConnFault
Group Fault: No Faults
Motion Fault: No Faults
Initialization Fault: No Faults
Attribute Error: CIPAxi***eptionAction - Invalid Attribute Value.
Start Inhibited: Not Inhibited
Motor Catalog: TLY-A110P-Bxx2
I have gone through the manual numerous times but I am certainly missing something simple.Any help would be appreciated thank you.
Solved.
F.Y.I
I managed to solve my issue. It was a firmware incompatibility issue. I had upgraded the PLC's firmware to 21 and assumed the drives would be ok. But alas, unfortunately not. I had to upgrade their firmware as well.
Now all is well.
Thought I would let you all know.
Happy programming!
Just an explaination for anyone else with the same problem. There is a bug with Kinetix 350 firmware v1.47 or earlier when using CompactLogix firmware v21 and a TL-Series servo. TL-Series servos will not work with Kinetix 350 unless the Kinetix 350 firmware is upgraded to v1.55 OR the CompactLogix firmware is downgraded to v20.
Hello Everyone hardware: 1769-L36ERMS Compact GuardLogic 5370 Safety Controller, revision 30.014 drive: 2097-V32PRO-LM Kinetix 350, 2A, 240V...
1,867
Hello, First thank for all the help i've gotten through this forum over the years reading others threads. I'm having an issue with Kinetix 5700...
5,896
Good Morning , I'm having a problem with a Kinetix Servo MAPC instruction. I keep getting a #85 Fault. Could you give me some...
1,691
1,128
Why the Position Loop Bandwidth, in Rockwell axis of Kinetix 5700 Servo Drive, is in Hertz ? Same for the Position Integrator Bandwidth . What is...
2,708