Rockwell Product Safety Alert
Canmaker
Jan 2005
Yorkshire UK
I'd like to alert everyone to a Product Safety Alert issued by Rockwell on 2nd April 06. This concerns PLC5's when programmed with RSLogix5 version 6.3 or higher.
If you download a program to a PLC5, or do an online edit connecting to the PLC using a KTX(D), KT, PKTX(D) or PCMK Driver and using RSLinx version 2.50.00.20 (the version distributed with CPR7) There is a possibility that the PLC program can become corrupted. There is a patch avaialble (for the RSLinx Software) from the Rockwell Knowledgebase - search on Google for A149859552
I am still trying to find out if this affect SLC as well as PLC
Maybe I am harsh, but in a different industry, wouldn't this be called a "product recall"
We had to upgrade to RSLinx 2.50 to program a new Micro 1100, only to find that we had to install hotfixes as well.....
There is a possibility that the PLC program can become corrupted.I wonder what that means. 6 months ago, I was working on a PLC5 and setting up BTR/BTW blocks. I thought I had done something really wrong and ALL of the outputs (5 modules worth) starting firing on and off really fast. Contactors were arcing and we ending up blowing 5 of them. It was kind of pretty with all of those blue arcs going off.
Doubt it. The corruption was evident by the processor having a major fault and shutting down. Rapid-firing of contactors while programming Block Transfers is more likely programmer error (wrong RGS).
If it were cars or cribs, it would be a product recall. In the world of high-level application programming, the strategy is - find a bug, and announce it after the patch is ready.
I asked our IT expert what they call it when Microsoft does this, but he said there isn't a word for the practice. Ergo -
We need to make one up!
Just as Horace Walpole coined the word "serendipity", meaning "finding or discovering something by accident". He got the word from an old fairy tale about Sri Lanka, called "The Three Princes of Serendip", where the princes were on a journey and constantly discovering things by accident.
So come on all you ingenious techies. If anyone is qualified to create this word, it's us. When we get enough suggestions, Casey can put up a poll and we'll vote, then submit it to webster's.
Definition - "To cover up or conceal a problem until a solution is prepared."
TM
If all outputs in one module works strangely, then the cause is possibly a bad connection in the connector between the module and the chassis backplane (*).
If several modules are affected, then the error can be in the connector between the CPU and the chassis backplane (**).
This is a known weakness in the PLC5. The remedy is usually to remove and reinsert the modules or the CPU a couple of times. This gives the connector a "massage" and everything will work again, for a while at least.
Have experienced both of the above.
*: For a single module, then also look for wire strands or such for having entered thru the openings in top of the chassis/module. Once had a nasty error from a thin wire strand falling into a module, making all kinds of funny games.
**: For several modules, there is also the possibilty that the chassis is defective.
There is also the possibility that the cause was wrong programming of the block transfers so that the wrong module would be affected. However, I cannot see how this can affect several modules as a block transfer targets one particular module and not several.
All this has nothing to do with the thread starters post though. Sorry.
Hmm, it occurrs to me the definition is too broad. How about:
"To cover up or conceal a problem or defect in a consumer product until a solution is prepared."
I thought about pharmacy companies, for instance, "mercking", but the difference here is that the company actually plans to release a fix for the issue. Drug companies just hope statistics are with them and they never get caught. That's just a "cover-up".
TM
TimothyMoulder said:
Just as Horace Walpole coined the word "serendipity", meaning "finding or discovering something by accident". He got the word from an old fairy tale about Sri Lanka, called "The Three Princes of Serendip", where the princes were on a journey and constantly discovering things by accident. TM
Tim,
You must be a logophile. Do you read the OED (Oxford English Dictionary) for fun?
Dan
The effect of the RSLinx 2.50 / PLC-5 DH+ bug was not malfunction or unintended operation of the PLC-5 program, but corruption and subsequent erasure of the application program. If the controller finds out during the once-per-scan checksum routine that the program edit wasn't made successfully, it faults and shuts down because it can no longer guarantee that the program will function as intended.
This bug didn't affect SLC-500 users. It didn't affect MicroLogix users. It didn't affect users of RSLinx 2.41, 2.42, or 2.43, nor users who access their PLC-5 controllers over Ethernet or ControlNet or via a ControlLogix bridge.
danw said:
Tim,
Dan
No, but I did read Ambrose Bierce's "The Devil's Dictionary" cover to cover. I picked up a good bit of trivia - for instance, the art of "flaming" on the internet should properly be called "logomachy".
My personal favorite (warning - politically incorrect)
"witch", n., 1. An ugly old woman in a wicked league with the devil. 2. A beautiful young woman, in wickedness a league beyond the devil.
TM
Were you ONLINE editing when this happened? When you hit the verify button, your edited BTR/W addressing will take effect (the software changes the contents of the control address to your new logic's contents) BEFORE you test and assemble. That has bitten me a couple of times, luckily no damage occurred in my cases.
Okay, back on the subject...
Let's see, "To cover up a problem until a solution is found..." ...gee this is so common, it's hard to pin it on one company name.
While we are at it I need a word for "to create problems in order to generate future business providing support and solutions"
And how about "to promote the incompetent to positions where they can't do any product damage"
My suggestions
"To cover up a problem until a solution is found..." : Iiby (from Ignorance Is Bliss)
"to create problems in order to generate future business providing support and solutions" : Redmondate (from a certain well known software company)
"to promote the incompetent to positions where they can't do any product damage" : This one is tough. I thought of the Peter Principle first. How about Corporify (similar to "Promoted to corporate headquarters.")
Thomas
Rockwell Product Key Location on Computer I would like to know where Rockwell stores the product key on a computer. No, I don’t need to contact...
29,938
I am trying to use the Rockwell Product Configuration http://www.rockwellautomation.com/en/e-tools/index.html I am trying to configure a...
2,152
We had a Harddrive crash on one of our laptops. On reactivating RS Logix 5000 ver.16 and RS Linx 2.50 .Where can I locate the Product Key that it...
58,557
I am working on a large migration of the standard PID instruction to the PlantPAx P_PIDE. Has anyone done a migration like this before and have a...
76
Hi all. What is the purpose of that block (MVM) when used with a 2#1111_1111_1111_1111 mask in that situation? I'm really hoping there is...
147