nick88
I'm using a PID loop instruction in a Floboss 107 RTU for an oil and gas application. There are two loops, a primary and override loop - primary is for flow control, and override loop for pressure control. The PV's of the primary and override loops are from a USM meter and pressure transmitter respectively. The pressure transmitter is downstream of control valve, and USM is upstream of control valve. The output of the loop is a 4-20ma signal to a GE oil and gas DNGP valve. I'm using a low select between each loop, so which ever output is lowest should be in control. If flow or pressure is below set point, we want valve to open, valve will close when either PV is above SP.
I'm having an issue with the loop select toggling between two loops. Our PID controller was in pressure control for the past several weeks with SP's around 684 psig and 165000MSCFD. The flow was around 40000 MSCFD, pressure stayed at 684 psig since we were in pressure control.
When operators raised pressure SP to 720 psig (flow sp remained the same,) the pressure raised to around 702 psi and flow jumped up to 100000 MSCFD when the loop select started toggling between primary and override. The issue is the primary flow control loop was trying to close valve and pressure loop was doing just the opposite. Valve position remained at around 59% open due to the toggling action.
Is there anyway to adjust parameters so that the pressure loop remains in control until the flow PV is 10000 MSCF or so from SP and the flow loop starts to take action?Here are other configured variables in PID.
Primary Variable EU Span 0 - 200000 MSCF/DAY
Secondary Variable EU Span 0 - 1500 PSI
Output Span 0 - 100 % (0% = close)
Loop Period - 0.5 seconds
Primary Deadband - 300.0 MSCF/DAY
Override Deadband - 0.00 PSIG
Override Gain 27.0
Override Reset .1
Override Derivative 0.00
Primary Gain 2.3
Primary Reset 1.4
Primary Derivative 0.00
Nick