rosemount temperature 248
shkoko2000
May 2011
cairo
296
hi all,
please i need to ask about connection of three wire RTD to this transmitter when i look at the manual and found the connection as the attached pic, so i performed that then the hart gave sensor fail.
when i connect jumper between therminal 1 and 2, the reading becomes normal,
why this issue happen?
can anyone illustrate?
I'm not sure why it says to leave it empty as most of the time if it has 4 wire input and you have a 3 wire rtd, the jumper is installed to the 4th terminal.
Could it be an issue with terminal numbering? If you declare thdt it is 3 wire and it has no connection then it faults. Or is it setup for 4 wire so it needs the jumper?
Or it could be a mistake in the manual.
Look at Post #21 in this thread:
http://www.plctalk.net/qanda/showthread.php?t=100074&highlight=Rosemount&page=2
where I posted a screen shot of an error I found in Rosemount's 644 temperature transmitter manual. Polarity is backwards.
Another major instrumentation vendor private labels their DIN rail mount and head mounted temperature transmitters and has similar issues with mistakes in the manual.
hmmm. Dan I think you.are.onto something. I had the same issues with a Fisher MVS205R which is also Emerson
Hi, a customer has an installation on which a Yamatake DCS monitors about 60 Rosemount FF temperature transmitters. The DCS is a Mobdus RTU master...
585
The original Rosemount pressure transmitter was configured to give them the 5 million gallon tanks level in inches. It died so they put in a...
3,618
The rosemount 8712 flow meter is displaying coi open circuit. Should iI just replace the sensor? I looked in the troubleshooting and only thing im...
4,818
Hello everyone, I am working with a 8705 flow element mounted to a 8712 remote mount transmitter. From my previous experience with Rosemount...
3,251
Hello, Is there a way to set the output of ultrasonic level device to show high level when the sensor drives the analog signal to a saturation...
3,038