Hi all
I have a lahuer screen connected to a Allen Bradley SLC5/03
with a RJ 45 connection. There are only 2 cores used and I was hoping that I connect it to a serial port in SLC5/05 if I set up the port as a 485.
If anyone knows if I can do this would you also know which pins to connect to. I was going to connect it to pins 2 and 3 but not sure if this would work.
Thanks again to everyone
Donnchadh K
Reading that thread may help you distinguish between Data Highway 485 (the protocol) and RS-485 (the electrical signalling method).
To connect that display to an SLC-5/05, you need a signal converter. The Allen-Bradley 1761-NET-AIC is ideal.
There should be three (3) total wires between your display and the SLC-5/03 port; Data A, Data B, and Data Common. It's possible that your display doesn't have a dedicated Data Common, in which case it's probably using the shield or Ground.
The 1761-NET-AIC has a screw terminal block to land the Data A, Data B and Data Common wires onto, then you can connect it using an ordinary null-modem type cable (1761-CBL-PM02 or 1747-CP3) to the SLC-5/05 serial port.
Hi BB and Ken
The AIC worked perfect and I now know what the AIC is for and where I would use it. I had an old one that I had removed from a plc panel, must be 3 years now.
I am replacing the 5/03 with a 5/05 and a Panel view Plus 1000.
The AIC is only a temp til the operators and tech are happy with the new screen ( a just incase)
Thanks again for your time and reply.
Donnchadh K
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
223
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
119
Does anyone know of an AOI using the user ASCII protocol select on the L6x controllers that will talk Modbus RTU using RS-485? Thanks, Trevor...
141
Hello, I'm trying to delve a little into rs-485 communications for a couple projects of mine. Until now I've been using a delta vfd and a delta...
125
Hello, I need to access the bits from the fire system control panel through RS-485. So, I used Read Var block to read from the panel...
199