Rs485
angi
Jan 2010
us
361
Hi Guys
there is a RS485 interface and a dip switch used to set address for in a motor drive, in its operation manual , they did not mention what protocol could be used to communication with it, could I use Profibus protocol to control it?
thanks
There is a yellow wire going out from out of a switchboard and I want to know could I wire a lamp to it?
Hey, please provide some info, otherwise - my cristal ball says "Oh, yes it is really 485"
You need to determine the make and model of the drive and share that with us if you want some advice.
In my opinion, there's a 30% chance it's Modbus RTU and a 5% chance it's Profibus DP. That leaves a 65% chance it's a proprietary protocol specific to this model of drive.
I will be clear so that there is no chance of misunderstanding:
You are not posting enough details for Forum members to help you.
Posting that this is a "MOVIDRIVE" is more helpful than posting that it is a "motor drive", but you need to post real details, like the exact and complete model number.
Describing a connector is not very helpful. Providing the connector label name or a photograph of the connector is helpful.
Stating that information is not in the user manual is not very helpful. Posting the exact Publication Number of that user manual and the sections you have searched for this information would be more helpful.
If the following link is the user manual for the Movidrive you are using, then the MOVIMOT serial protocol is described in Chapter 7:
http://download.sew-eurodrive.com/download/pdf/17000017.pdf
This protocol is not Profibus, and it is not Modbus.
hi Ken
sorry for the confusion, this is the manual I have here, just like you said it is not a Profibus and not a Modbus, so if I want to connect with AB PLC, how to do that?
I missed Mdim's replay, maybe we need install a communication module on the drive.
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
258
Hi, Seeking consultation on an implementation matter, and have a question about Modicon Compact 984 communication through RS485: Three Modicon...
252
i have an device which can support serial (RS485,RS232),CAN protocol . i want to connect it to an existing MIB 1553B bus ,what device will I need...
105
Hi all, I am trying to do Modbus communications via the CB1241 RS485 Communication Board on a Siemens S71200 PLC. I am using a 1215C CPU. After...
278
I'm trying to use a Red Lion Cub counter (Cub5B00) as a counter and give the cub's counts to a Graphite G12 PLC/HMI to display. After about an...
121