rslinx as a service?
joeparrish
Nov 2007
owensboro ky
161
We have a vm running factorytalk se on that we have rslinx so factorytalk can talk to a slc 500.
When we loose power to the plants we have to turn rslinx off and on to regain communications with this rack.
Currently rslinx is set to run as a service
tech support is saying this should not be run as a service although all of our other servers are running as a service
I cannot try this until the plants are down so I am trying to get any other info on this, I read the rslinx manual and it makes no mention to running as a service or not
That's AB for you.
Unless something has changed recently, Rslinx is set to run as a service by default.
On every pc I have looked at / installed it on, its set to run as a service.
On the programmers pc's, it is NOT running as a service.
We have to change the communication configuration almost every time we hook up to a plc.
regards,
james
I understand how to change it what I am trying to understand is should it be set as a service or not
every computer we have running has it set as a service and have had no issues anywhere else
I guess i want to know when to run as a service and when not to
In Rightclick Mycomputer -- Manage -- Services and applications : what setting you have applied for RSLinx i.e. Manual or Automatic???
Try by chaning this setting.
I just looked at a recently configured station that is running FactoryTalk SE and it is set as follows i Services:
RS Linx Classic: Manual
RS Linx Enterprise: Automatic
Another thing to check - when you start RSLinx, select the "RSLinx Control Panel" in the Start/All Programs menu - when the control panel starts there is a check box to select Always Run As A Service. If this is checked RSLinx will auto start with Windows as a service.
I found this out because you can not add a DF-1 driver in configure drivers if running as a service.
Hey Folks, I am facing an issue with rslinx classic (gateway) , wherein the "always run in service mode" checkbox does not appear on the...
1,226
Hey all, I've just set up our new laptop with RSLinx, but I cannot get it to work as a service. When I run the RSLinx Launch Control Panel, I...
5,872
Hi, I am using RSLinx Classic V 2.59 running on Windows XP Professional SP2. I am using OPC Test client to connect to RSLInx OPC Server but :-...
4,222
I just installed rslinx oem. I used to have lite. We got OEM so that we can send data to an OPC. I want to run linx as a service but I cant...
4,092
Does anyone know why the newer (>3.51) releases of RSLinx, when running under vista or 7 don't have a GUI when running as a service? Is there a...
3,911