RSLinx DF1 Autoconfigure to PLC5/40 not working
pcola
Nov 2005
pensacola, fl
22
RSLinx 2.43 has been installed on my computer for months, but now when I try to autoconfigure a DF1 connection to a PLC5 Channel 0, the message "Auto Configure Initializing" appears and it does not continue. I unistalled and reinstalled, but it has made no difference; the one change has been the installation of RSView Studio ME. Any comments?
Is the AB-DF1 driver running?
Do you have the correct null-modem cable connection?
Do you have any other drivers configured and if so, what are they?
The advice given by rgurin is excellent as usual, and absoutely correct. If you need to get going in a hurry, CTRL>ALT>DEL and look in Windows Task Manager. Under processes, look for RSLinxNG.EXE; highlight it and click End Process button. Then try to autoconfigure your DF1 driver in RSLinx Classic.
Sometimes your COM port does not communicate without any reason. Try to Disable the COM port and Enable the Port again and restart the computer. This Problem is very Typical with Panelviews.
Go in device manager, disable com port, go in advance settings & change the com port no. to 5,6 or higher ....many times on com 1-4 there is lot of traffic that results in error.
It's also important to clarify that the operation is actually locking up, and not failing. Usually the timeout for this takes at least 30 seconds, if not one full minute if I am not mistaken. I personally have never seen the operation lock up, only fail because of the reason's mentioned above, or because the incorrect cable was being used.
My experience is with a SLC, not a PLC, but still similar...
I was having a similar issue with Linx not communicating or browsing the netowrk. Linx would actually lock up entirely whenever I tried to Auto-Configure. I later found out that Simatic was setup on the same COM port,a nd they were interfereing. Maybe try changing to a second COM port, if you have one.
Trying to recover an old well controller ML1000 using DF1 Half Duplex and my RSLinx won't allow me to create a DF1 Polling Master Driver. I am...
1,504
Has anyone run into a situation where RSLinx comms was successfully setup with a SLC500 PLC on Channel0 (DF1 driver, 19200) and upon opening...
1,693
Hi, I am new to PLC. Got a Micrologix 1000 with RS232 cable. Installed RSlinx on XP with SP2. Try to connect PC to ML1000 with DF1 protocal. Get...
16,986
Folks, A SLC503 used to be connected to the Internet via a Digi One IAP. During program download to the PLC the Internet connection was...
11,945
Dear all, i have to access the data of SLC at DCS End through RS232 port . SLC and DCS is connected through fiber optics.When i configure the...
3,722