If I connect to SLC 5/05 or ML1200 using RS-232 DF1 Devices driver and click on the Autoconfigure button, I get a message saying "Autoconfigure Initializing", but it won't go further than that. Used to work fine.
It doesn't appear that anything else has control of the COM port, and RSLinx works fine using Ethernet drivers.
Any suggestions?
Your RS-232 cable could have a broken wire (internal break). Cables that are flexed many times eventually have a break in one of the wires. Most times you can't see it from the outside. Test the cable.
Is the installation of SP3 recent ?
If the various baud rates, parity options, and error checking modes show up in sequence then it's probably a bad cable or bad port.
But if it just goes to "Autoconfigure Initializing", I would say that RSLinx is having trouble sending the port settings to Windows, which sounds like an XPSP3 problem.
There has been some discussion on this and other Forums about a trick to roll back the SP3 serial driver by replacing it with one from an SP2 computer.
The other option is to try out RSLinx 2.56 and see if it has the same trouble.
GIT has a good point; conflicting drivers can cause similar problems.
When you have another driver running, like a DF1 driver in RSLinx Enterprise or the 1747-PIC driver still in residence, or even a Modbus or other driver in separate software, the error is usually different.
"Failed to open COMx for configuration" is the usual error messaage in those circumstances. It might be different if the conflicting driver is actually inside RSLinx.
The lack of an error message does not rule out a driver conflict, but does point to a software condition that RSLinx doesn't have an error check for.
My first step would be to install RSLinx 2.56, and my second step would be to hook up a serial sniffer or just a serial breakout box to see if any traffic actually hits the pins of the serial port, or if it gets hung up inside the operating system.
If the fault is still persisting I wonder if its time to delete the 2 Harmony files normally found at
C:\Program Files\Rockwell Software\RSCOMMON
as these are cache file that get rebuilt when RSLinx starts.
Well thats my wild guess for something to try.
Tried sniffer first - didn't detect anything. Reinstalled RSLinx - didn't help.
I rolled-back the comm port driver - didn't help, either. Updating the comm port driver file did the trick!
Thanks for all your help.
I have 2 PLCs. One is networked to our plant, and the other is networked to the first PLC via a 1756-EN2T. I could easily get the second PLC...
63
Hi, I am working on a project, where I face a issue with respected to Network Dropout. The PLC is connected to a 16 port unmanaged switch, where...
220
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
251
Anyone have issues with RSLinx being very slow to open. It sometimes will say "Checking Activation" at the bottom for what seems like an...
179
I need to support some old data collection that is running on Excel, but I need to get it running on LibreOffice. The following statement works...
97