RSLOGIX 5000 Connection to PLC Via DH+
Alan64
Feb 2007
Nantes
24
Hello,
I've trouble trying to connect to a ControlLogix processor using a DH+ Link (I use PCMCK Card).
A DHRIO Card is in the local chassis and processor on slot 0.
I Connect my DH+ Cable to DHRIO CARD (station number is set to 10) ,browse the target processor in order to get the Path and as soon as I clic on Go Online I get ' No connection to that processor' message .
I did check the cabling and so on : all OK
As I can see the processor using RSLinx I think that the cabling is good.
Same problem if define the DH+ path as project path.
By another hand I can access the processor using Ethernet card (on same chassis).
It seems like the project can only be used online with Ethernet connection .
I've noted that the project name (the RSLogix PC file) is not same as project name in the Processor .
Is there someone that could help ?
Regards. Alan
Alan:
I seem to remember having a similar problem. The DHRIO card had a newer firmware and I needed to upgrade RSLinx before it would recognize it. The other option was I could have updated the EDS files on computer to recognize the newer firmware on this card. Check the firmware on card and see if it is compatible with your version of RSLinx.
Kim
DHRIO card is Series D , Firmware is 6.2
RsLinx version 2.43.01.23
RSLinx reconizes the card and, card definition in RSLogix 5000 Projects matches.
I had a look at the card properties (from RsLinx) and found no routing table and processor slot set to 0 .
Nothing special I think.
The exact text of the error message when trying to go on line is :
"Failed to go with the controler . No open connection"
Error : 701-8004250A
I'll try to update the DHRIO EDS to see.
Hello,
Is there any update on this issue since currently I am experiencing the same 'Error Message' as Alan?
"Failed to go with the controller . No open connection"
Like in the subject, I can't connect to the PLC, the Who active shows nothing just like RSLinx, you can see it in the attached picture. Its been...
1,678
Ive recently been having trouble with the stability of my connection when online with a plc, The software intermittently freezes (cogwheel...
2,070
Hi All, I am working on a project which uses compactlogix PLC and Citect SCADA. I don't have physical PLC at the moment. Need to test tag...
5,597
Hi all, I have 2 Allen-Bradley CompactLogix PLCs (1769-L35E) talking to each other over ethernet. One is producing tags, the other is consuming...
8,892
rslogic 5000: I need to setup a alarm to detect if Ethernet has lost connection I have searched everywhere on the net and can not find out how to...
3,896