Hello, all.
This is my first time working with a ControlLogix and RSLogix 5000 and I am having some trouble with the PID ladder function. I was in the field today with the processor in run mode and I will be back there again tomorrow to try to resolve this.
The PID will be used to control the speed of VFD-driven pumps based on header pressure. I have configured the PV, SP, and basic parameters of the PID instruction.
Once I moved from checkout of the manual routine and the physical I/O, I noticed that the PV was not updating in my PID block. The PID is in a continuous task, so I found out quickly that I needed to include a timer to trigger the PID. Once I included the timer logic, the PID became "live" and the PV updated continuously. The timer and the loop update time are configured for the same time, 0.250 seconds.
At the exact moment that I accepted the timer edits and the PID went live, the "Output %" of the PID went to 100%. Mind you, the PV was much higher than the SP. Here are some additional notes:
- PID is running in Auto.
- None of the tuning constants have been configured yet (all zeros). I actually changed these (mainly the proportional) to some large values just to see if I could get the output to drop from 100%, but no go.
- Please see the (2) attached screenshots of additional configuration.
- The Set Output value is set to 100%. I tried to change this, but it goes right back to 100%. It seems that if I change the CV High Limit, the Output % changes to match it.
Can anyone help steer me in the right direction? I will be onsite again in the morning and I am concerned that it will be an all day affair trying to figure this out.
Thanks!
Justin
This is my first time working with a ControlLogix and RSLogix 5000 and I am having some trouble with the PID ladder function. I was in the field today with the processor in run mode and I will be back there again tomorrow to try to resolve this.
The PID will be used to control the speed of VFD-driven pumps based on header pressure. I have configured the PV, SP, and basic parameters of the PID instruction.
Once I moved from checkout of the manual routine and the physical I/O, I noticed that the PV was not updating in my PID block. The PID is in a continuous task, so I found out quickly that I needed to include a timer to trigger the PID. Once I included the timer logic, the PID became "live" and the PV updated continuously. The timer and the loop update time are configured for the same time, 0.250 seconds.
At the exact moment that I accepted the timer edits and the PID went live, the "Output %" of the PID went to 100%. Mind you, the PV was much higher than the SP. Here are some additional notes:
- PID is running in Auto.
- None of the tuning constants have been configured yet (all zeros). I actually changed these (mainly the proportional) to some large values just to see if I could get the output to drop from 100%, but no go.
- Please see the (2) attached screenshots of additional configuration.
- The Set Output value is set to 100%. I tried to change this, but it goes right back to 100%. It seems that if I change the CV High Limit, the Output % changes to match it.
Can anyone help steer me in the right direction? I will be onsite again in the morning and I am concerned that it will be an all day affair trying to figure this out.
Thanks!
Justin