How do i use the TON command to monitor the number of hours something stays on for? what would the preset value be in this case? Or is there another command that I should be using? I'm using RSLOGIX 5000 studio version 32. Thanks.
Since CLX timer presets are of the DINT type, the maximum preset value would be 2,147,483,647.
Since CLX timers operate with a mS timebase, that means that the maximum number of hours that can be accumulated in a timer is 35,791. (2,147,483,647 / 1000 / 60)
You may want to consider a different method for accumulating run-time hours if you want to log more than 35,791 hours. Perhaps a periodic task that operates once per minute and adds 1 to an accumulator register whenever the motor is running, then divide the value of that accumulator register by 60 to convert from minutes to hours.
There are many methods for tracking run-time, and the choice depends upon the required accuracy and maximum number of hours you desire to keep track of.
In Logix5000 processors, i always liked using the GSV function to monitor the system clock, and calculate an hour meter from that. You can use a oneshot to check when the last bit of the seconds goes from 0 to 1. That will mean 2 seconds has passed.
I think you missed a 60 in your division: 2,147,483,647 msec / 1000 msec/sec / 60 sec/min / 60 min/hr = 596.52 hours.
We do something similar with a one-second periodic task, counting seconds when the motor is running. When the count reaches 360 (0.1 hour), the program adds 1 to the DINT runtime and clears the count. The OIU or SCADA tag is scaled by 0.1 to display actual hours.
I've done that too, back when Version 13 redundancy only allowed continuous tasks.
I set up the RTO with a .PRE of 400000. Use the RTO instead of TON in order to not lose the time that is accumulated when the motor turns off.
When the .ACC is >= 360000 (6mins), I increment a DINT (HourMeter) and then subtract 360000 from the .ACC. This allows the time to continue running without losing any time and provides an hour meter that is in 1/10ths which is what most are used to seeing.
Keep it simple.
A RTO with a .pre of 3600000 will count hours, when .DN, use this to increment a CTU, when incremented, reset the RTO.
So many ways of killing this cat (excuse the analogy).
So many programs I have seen have totally ignored what happens if the processor restarts. Ordinary timers are reset, non-retentive output bits (OTE) are turned off, FAL and other "Controlled" instructions are reset, such a lot happens.....
Just forget TON, that loses its data if the processor is re-started. You have to use RTO.
You will use that timer to increment a counter, counting whatever time period you want to work with. It depends on your timebase, what do you need to know ? How many minutes the device has been active, how many hours, days, or even weeks.
Set the PRE to the appropriate value, then count how many times it has "timed_out" or .DN. Reset the timer, and count up the running time counter.
Simples ....
I have been using this method since the PLC-5 days, works great.
Yes, many ways to do this.
My method as below. I put all my time calculations in a Periodic task of 1000ms. It gives results in Hh:Mm;Ss format
This is what I do, but I use a preset of 36 seconds and imply two decimal places so my long integer is hours to the 1/100th
Hi, I'm just looking for a simple way to make a button in excel (via VBA I presume) to toggle a bit in RSLogix 5000. I just got FactoyTalkLinx...
570
Hi, So I have one push button(non-latch momentary) and would like use it to trigger two function sequences with the short press for primary...
2,010
How can I add the "Go To..." function to the RSLogix 5000's Standard Toolbar?
3,610
Got into a bit of a debate the other day, and wanted to get some gurus' opinion/expertise on the subject. When duration of an output's ON (or...
10,775
Hey, Can someone tell me what the default time base is for TON timers in RSLogix 5000? In the TON timer I don't see the option anywhere to edit...
43,364