rslogix setting up a PID logic block
Jrivers010
Aug 2017
Washington
20
spefically, its the allen bradley free version and/or the 500 version.
for the PV on PID, does the input go there or the scaled value? I cant find any exact simple explanation.
I have the Udemy courses example that the instructor wrote, but i am not sure if i am allowed to post that up, as it might be copyright infringement?
using the emulate software for the testings.
unless they've changed it, I'm pretty sure that the emulator won't actually "run" the PID instruction ...
the "input" (the analog signal from your input module) should be entered for the PV ... and that signal SHOULD be scaled to a range of 0 to 16383 ... specifically, the PID for your type of system (RSLogix 500) expects its input (PV) signal to ALWAYS have a range between those values ... anything other than that MIGHT work - but will give less-than-optimum operation ...
so ...
if the input module is not capable of automatically producing a signal within the range of 0 to 16383 then you SHOULD provide the necessary math to convert the module's data signal into that range before presenting it to the PID's Process Variable entry ...
Hi all, I have an issue with 1756-L62S (revision 20.13) safety lock. We can't figure out who put safety lock on our project. Before I try...
1,028
2,431
Hi there, Does anyone know how to limit the # of decimal places of all floating integers displayed on the HMI? I want to display one decimal...
7,468
Hi I am using compactlogix and I would like to view the some of the plc setting like running times ect back in our office, I have Ethernet going...
10,254
Alright, here is what I know. In the lab we are building a new OSIsoft PI system and need to inject some real life data into the machines for...
11,738