I think you are on the wrong track...
From the Instruction Help.
.OV
BOOL
The overflow bit indicates the counter exceeded the upper limit of 2,147,483,647. The counter then rolls over to -2,147,483,648 and begins counting up again.
This is a flag, not a control.
If you want to programmatically reset a counter, use the RES instruction.
If you want to reset the counter as soon as the accumulator is >= preset, then use the .DN to RES the counter.