Ken Roach
Lifetime Supporting Member + Moderator
I was intrigued by this and set up a demo system at my desk:
RSLogix 5000 v13.04
Owner Controller:
1756-L1 v13.27
1756-ENET/B v2.7 IP Address 192.168.1.7
Listener Controller
1756-L1 v13.27
1756-ENBT/A v3.9 IP Address 192.168.1.101
I/O Adapter
1794-AENT v2.12 IP Address 192.168.1.94
1794-IB16
1794-OB16
1794-IE4xOE2
I set up a program called "FLEX_Owner" and another called "FLEX_Listener".
The Owner program has a "None" connection type for the 1794-AENT itself, and Module Connections for the three I/O modules. The discrete modules are at 50 ms, the analog at 100 ms RPI.
The Listener program has a "Listen Only - Data" connection for the 1794-IB16 and an "Listen Only - Input Data" connection for the 1794-IE4XOE2.
Put 'em together, download, and the FLEX_Owner program has happy I/O connections and data's coming through.
But the FLEX_Listener... has "Module Fault (Code 16#0118)Module Configuration Rejected: Format Error" in the Connection tab for both connections.
But wait... the whole point of the Listen Only connection is that there isn't supposed to be Configuration data going out to the 1794-AENT for these modules.
RSLogix 5000 v13.04
Owner Controller:
1756-L1 v13.27
1756-ENET/B v2.7 IP Address 192.168.1.7
Listener Controller
1756-L1 v13.27
1756-ENBT/A v3.9 IP Address 192.168.1.101
I/O Adapter
1794-AENT v2.12 IP Address 192.168.1.94
1794-IB16
1794-OB16
1794-IE4xOE2
I set up a program called "FLEX_Owner" and another called "FLEX_Listener".
The Owner program has a "None" connection type for the 1794-AENT itself, and Module Connections for the three I/O modules. The discrete modules are at 50 ms, the analog at 100 ms RPI.
The Listener program has a "Listen Only - Data" connection for the 1794-IB16 and an "Listen Only - Input Data" connection for the 1794-IE4XOE2.
Put 'em together, download, and the FLEX_Owner program has happy I/O connections and data's coming through.
But the FLEX_Listener... has "Module Fault (Code 16#0118)Module Configuration Rejected: Format Error" in the Connection tab for both connections.
But wait... the whole point of the Listen Only connection is that there isn't supposed to be Configuration data going out to the 1794-AENT for these modules.