Here is a post from about a week ago that has some screen shots
http://www.plctalk.net/qanda/showthread.php?t=49712&highlight=rsview
What is the PLC you are talking to. ?
When you go to tags on RSView ME, can you see any tags or do, you only see them in the graphics screens with curly brackets, and pointing to your PLC name. ?
YOU say you are using RSView Studio V3.2, I know you may need to keep using that version because of the age of your Panel View, but 3.2 was superceeded by ver 4 which was alot easier to work with, and Studio and Panel View are now up to ver 5 .
This below does refer to RSView 32 but the same structure applies for RSView ME and has been used by other posters on RSView ME
This I have posted before.
Sometimes when edits are done in RSView 32, the project just does not want to release the cache files, and tries to keep running on previous settings.
A repair I do if any issue crops up, is to shut down the project, then in windows explorer, go into the project folder, open the cache folder, and blow away all files in that cache folder, they will be rebuilt on the next start up.
The next thing I do is go to the projects Tag folder, and look for one file with "the project name".cac
I THEN BLOW THAT ONE ONLY AWAY, leaving all the other files in that folder, this .cac file also will be rebuilt on project start up.
Then shut down computer and reboot and run your project.
I cant promise this will fix your problem, but it wont harm it either.