When I've done projects using RSLogix 500, my PV+ tags were addressed as ::[CONTROLLER]B3:0/1 etc.
Is the address structure using RSLogix 5000 the same except for replacing the bit address with a tag name in the controller?
Thanks for any help on this.
Generally, yes. Two things to watch out for, if the Logix tagname doesn't contain a ':' character, you should not have) the '::' prior to the device access name.
If the tagname does have a ':' character (such as resolving a Program scoped tag rather than Controller scoped), then you do need the '::' prior to the device access name.
Thanks for your help. You just solved my problem by mentioning controller scoped tags. All my tags were program scoped and would not be recognized by PV+.
I believe that's actually part of the "whole" OLE/OPC address. If you're networking to a tag-server that's running on a different computer there will be other address pieces between the :s. Kinda like the .s in an IP address. When you're running locally, you can leave those other pieces out, but still have to have field separators.
rPraveenkum said:
PV+ is connected to Ch0 of SLC or logix processor?
I'm using the Ethernet/IP port which is connected to a switch along with the PV+ and the laptop. I created a one button application to turn on a bit in the CompactLogix controller just to keep things simple. As soon as I changed the tag from program scope to controller scope, the button worked.
Program scoped tags can be read, you just need to completely resolve the scope, and then preceed the overall access with '::' again, as the ':' is the program scope resolution operator.
For a program scoped tag:
::[IO_Server]Program:MainProgram.The_Tag_Name
Hi Guys, Is there a tag search function in RSView Studio similar to the old function that was available in Panelbuilder 32 where you could...
3,048
Hey Guys , why if I am creating project for Panalview1000+ ( using studio) and on one of my screen there is a button "Start-Stop machine" and want...
1,414
I have RSVIEW STUDIO 6.1 and RS5000 R19. If I have the tags created in RS5000 and work on a screen in RSVIEW, I can see those offline tags...
6,078
I have created a Compactlogix PLC program with RSLogix5000, and now want to export the tags to PanelView Plus program created with RSView Studio...
11,564
Hi all, First time poster here... until a year ago my ladder logic exposure was at a GM assembly plant in the early 80's, all on D size paper...
4,774