RSViewStudio ME Enterprise Setup

Yokes9

Member
Join Date
Dec 2007
Location
Staples MN
Posts
8
I have been trying to connect a SLC 5/04 (logics 500) and a AB PV Plus 600(ME). I use a null modem cable to connect to the computer to the PLC, a straight through serial cable from PLC to PV, and the PV to computer with an ethernet. I've been trying to get this to work off and on for some time now.

I need to figure out how to correctly set up a shortcut In RSview Studio ME. This is what my communication "Local" looks like.
Local.jpg

(The computer browsed and found this all)

This is what my "Target" looks like.
Target.jpg

(The serial DF1's I added myself while experimenting)

I'm not sure how to set this shortcut up so my PV and PLC will communicate (RS Studio is new here this year so no one knows how to set this up). I've writen the Programs for both devices and set up the binary. I don't have class again till monday but I'll check this at home tonight and tomorrow. Thanks!
 
When you set your Target path you are defining where the HMI should look for the PLC, not where you are looking for the HMI. On the Target screen, highlight the PLC and then save the shortcut. You will need to download to the HMI, making sure that the Replace Communications box is check.

Keith
 
Local is how your PC talks to the PLC. This is for development purposes and has no impact on the PV+. As mentioned, the Target is where you configure how the PV+ gets to the PLC. Only the target gets downloaded to the PV+.

OG
 

Similar Topics

Hi I'm trying to browse online tags in my v16 L31 CompactLogix from an RSViewStudio PVP600 project. It seems not all the tags I am creating in...
Replies
2
Views
4,405
Trying to understand what the major difference is between FactoryTalk VeiwME and FactoryTalk View Studio.
Replies
3
Views
1,592
hi guys ,need help how to connect scadalarm on the RsviewStudio,will it support to start DDE...thanks..what is the Default DDE Application...
Replies
7
Views
2,986
I've devoleped a VB application for retrieve data from an Access database and now I wont write this values to some tag into my RSView studio stand...
Replies
1
Views
3,947
we have same HMI 2PC / SET LOCAL STATION version 9.0 patch 2021.dec and win10 pro v18.xx 1pc install logix5000 v19 v20 It was going well...
Replies
0
Views
212
Back
Top Bottom