RTD Module question
ceilingwalker
Mar 2010
Phoenix, AZ
1,586
Good day all. I would like to know if anyone might know why the Control Logix RTD modules do not require a drain wire (shield) connected to it, but the SLC500 module does? I assume it's because the SLC uses a back-plane and the Control Logix does not. Thank you.
A shield is not required for either system, they will both work without it. But is is recommended for noise reduction on any analog wiring.
Ok, thanks Mickey. Would you happen to know why my RTD Module has 6 "shield" connections on it and only 4 channels? I'm reading the book but it isn't specified.
Convenience.
What is the complete catalog number of your module?
Ok, so I don't need to run a ground wire to the module, right? I beleive I read in the book that it gets the proper ground from the back-plane, but now I can't find where it said it.
See exert from the manual below and make sure the chassis is grounded properly
It is convenience.
We don't bother usually with any device (PLC Module, Drive, Encoder etc) shield connection. We typically terminate the shields only at a single grounding buss running under the connection terminal strip in panels, and leave the other ends isolated by heat shrink tubing.
Life has gotten much better in the past ten years or so with regards to grounding shields, but still, a noisy ground loop can result in hours or days of searching.
Good day all, I changed the configuration of an RTD Module and when I resumed the program the system had a fault and shut-down. The module is a...
4,778
Good day all. I have an RTD module for a SLC500 5/03 that I can't get the temperature values to stop jumping from one temp to the next, on the HMI...
4,676
Hello all. I have two RTD's in the same acid tank. One reads 104 degrees F and the second is reading 54 degrees F. They are both at the same level...
1,944
Hello! I have RTD sensor with 4 wire and shield ( 2 red wire + 2 white wire + Shield) and I want to connect to 1734-IR2 module. But in the manual...
1,439
Hi everyone, I want to know if there is any possibility of correct a temperature offset directly in the RTD module. I have a system connected...
1,994