s400 logging data
Lesa
Sep 2006
Novi Sad
71
Hello guys,
I have a problem with one inverter. It suddenly turns off. We can not find cause, everything seams to work just fine.
I would like to log data from PLC on every scan cycle, to determine what is happening. I would like to log:
-swithces statuses
-status word
-control word
-setpoint
PLC is 412 and scada is wincc 6.0.
Do You have any advice how to do that?
Tnx!
What is the PLC scan time and how many scans are you going to store ?
Copy the code to a library and post on here for analysis.
Scan time is somewhere around 10ms and I would like to store few days of data. Frequency of inverter shut down is once per few days.
What code would you like me to submit?
I'm sorry but there are a lot of code in this projet and I need help with inverter shut down and how to log PLC data to determine problem.
Post it across several libraries then. Without seeing the code then guesswork about what/how to log isn't going to get you very far.
I would like to make some solution with current software, WinCC 6.0 and Step7 5.4 if possible if someone knows.
1.245,00 EUR is pretty much... :)
There is a demo version you could try not sure what the limitations will be.
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
1,516
Hello, I have two different PLC's. One being a 400 series siemens controller and the other is a L73 controller from RA. I am trying to...
1,301
We all know that the S7-300 range has been around for an age and the new S7-1200 & S7-1500 ranges are well established any one know if the...
3,823
So I have a USB to PPI-RS485 Multi Master Cable 1P 6Es7 901-3D830-0XA0 SC-W7K81802 Is this the cable I can connect my Windows 7 machine with Step...
3,464
Hi I need your help I want know that how many stations(wincc,op panel ,..) can connect to a plc S7-400 cpu417. According Technical...
2,302