S5 to S7 Conversion - Memory Map in S5-115U 943
TimH
Jul 2010
Johannesburg
The conversion goes well except for this:
A DB 31
L MB 195
SLW 1
T MW 202
L KH E43E <--- Where is this in the 943 memory
LIR 0 <--- loading direct from memory
L KF +20 <--- 20 memory locations later-is that 10 words?
+F
T DW 3
L KF -22 <--- 22 back
+F
LIR 0 <--- where is this?
L KF -16
+F
L MW 202
<F
BEB
L DW 3
L KF +1
+F
T MW 204
L MW 202
SLW 1
+F
T DW 4
L MW 204
TNB 4 <--- transfer back- is that right
L DR 10
T MB 194
And then later:
L MB 194
T DR 10
L DW 4
L KF -1
+F
T MW 204
L DW 10
L MW 204
TIR 2 <--- Where does this go to?
BE
Please help
Tim
LIR and TIR are indirect transfer instructions
E43E is in the block address list. I think should be DB31
I guess you will get the facit when LD is online, but till then my best guesses for the first bit:
A DB 31
L MB 195 Probably amount of words to be transfered
SLW 1
T MW 202
L KH E43E <--- Where is this in the 943 memory Start addr. for DB31 DW0
+F
T DW 3 Pointer to DB31 DW10
L KF -22 <--- 22 back +F
LIR 0 <--- where is this?Pointer to DB length (in the header - dont remember if it is bytes or words, i think it is words
L KF -16 Required space, probably bytes
+F
L MW 202
<F
BEB Stop if DB is to short
Kalle
Thanks guys,
MW195 seems to be the address pointed at.
I had worked out that E43E was pointing to the start address of DB31 - thanks for confirming that.
So pretty much I can use indirect addressing to get the same thing?
I know I can work it out, but maybe you gurus can tell me how to???
Thanks very much
To continue with MW195 - the FB is called elsewhere with coded like:
L KF +10
T MW195
CALL FB31 <-- that was the FB with the original code shown above
Elsewhere it was
L KF +50
T MW195
CALL FB31
Does that make sense??
It makes sense. The TNB 4 copies 4 bytes between the address pointers in AKKU1 and AKKU2, but I cannot remember which was the source and sink, and wheter you point to the first or last byte
. Anyone with good memory here?
Kalle
I found a manual finally. The source is in ACCU2, sink in ACCU1. MB195 must be an offset to the source. You don't have the description of DB31?
BEB
L DW 3 Pointer to DB31 DW10
L KF +1
+F
T MW 204 Sink
L MW 202 This is MB195 *2
SLW 1
+F Added to the sink pointer
T DW 4 Source
L MW 204 Sink
L DR 10
T MB 194
Kalle
Hi All I have just started a project to convert one of our machines from SLC500 to CLX5000. One of the first steps in the Rockwell guide was to...
1,997
I am trying to convert an Omron Syswin 3.4 format program to CX-Programmer, and then convert the PLC type within CX-programmer. I first converted...
8,839
I'm stumped by something seemingly simple. I want to move the numerical value of an ASCII style SINT into a REAL tag in Studio 5000. What's the...
84
I’m running short on time to complete this project (retirement looming), so thought I’d ask here hopefully save me some research time. I’m...
164
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
240