S7-1200 analogue module LEDs strange colour
BryanG
Feb 2005
Manchester
1,987
Just had a strange one on a 4 In 2 Out Siemens S7-1200 analogue module. I am used to seeing the status LEDs as green or red, but I haven't seen them as orange before. It seems that both the green and red are on at the same time, giving 'orange'. I have had my laptop connected and there are no error messages in the log and the CPU is reporting as fault free. I will swap out the unit anyway, but just wondered if anyone else had seen the same thing?
Did changing the card fix it?
Siemens manual also only states green and red... every now and then they have yellow thrown in the mix, but apparently not for the SM cards.
It seems that it was still working. This analogue IO doesn't do a lot yet, most of it is there for some future upgrades that my customer has planned. However at least one of the inputs and one of the outputs must have been working otherwise some of their machine testing would have failed. The output controls a 0-20mA air pressure control valve, and without that the main pump wouldn't have moved.
Like you say, very odd.
Swapped the unit and the problem went away. Only issue now is that the unit that was faulty on the machine works perfectly on the test rig. I will have to cycle the power a few times to see if it happens again.
Hi I am trying to find out if and where TIA Portal V11 provides "out of range" alarm for analog inputs. Do they just appear in diagnostics? I...
4,022
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
256
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
82
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
120
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
137