s7 1200 communication help
engea
Sep 2019
asasn
Hello,
Need help as I want to connect two s7 1200 cpus to extend I/O numbers.
The network will be 2 s7 1200 cpus and a regular pc as HMI.
What the best network configuration for it.
How much data are you transferring?
For up to a reasonable amount (256 bytes), I would use profinet with GET/PUT connection.
For get/put as I understand I need to to write a program to convert the data to the required I/O.
If right, is there's a way more simple so once I configure the network I can use all the modules directly.
You could set one up as an iDevice and read and write directly to it's IO.
Why not just buy remote IO rather than 2 S7-1200?
Or are you just working with what you've got.
Unfortunately yes I'm working with the available components.
I didn't configure an IDevice before.
Could you guide me through it.
I read it and understood the configuration criteria.
What I'm missing is when writing the logic how I'll deal with IO addressing for the IDevice.
For example if I've an input and output coil.
How I'll address this in the ladder.
Just use the I and Q bits configured in your hardware config.
.......I0.0.....................Q0.0
So if I've for the controller 8 bit out card
And the IDevice 8 bit out card
This mean if I want to call output from IDevice it will start from Q1.0
if the one at the I/O controller start Q0.0
Am I right
In the device that is providing its I/O you have to copy over states to/from the i-device from/to the physical i/o.
So, if you have for example:
Master PLC outputs configured for the slave PLC, Q100.0 .. Q101.7
Master PLC inputs configured for the slave PLC, I100.0 .. I101.7
Slave PLC i-device inputs I100.0 .. I101.7
Slave PLC i-device outputs Q100.0 .. Q101.7
Slave PLC physical outputs Q0.0 .. Q1.7
Slave PLC physical inputs I0.0 .. I1.7
In the Slave PLC you must program this:
I100.0 --> Q0.0 // from i-device inputs to physical outputs. edit: Possibly use DPRD_DAT for this, see below.
I100.1 --> Q0.1
etc.
I0.0 --> Q100.0 // from physical inputs to i-device outputs. edit: Possibly use DPWR_DAT for this, see below.
I0.1 --> Q100.1
etc.
In the master PLC when Q100.0 is activated, then Q0.0 in the slave PLC will activate.
And when input I0.0 in the slave PLC activated, then input I100.0 in the master PLC will activate.
edit: Not sure if it is an issue or not, since I dont have experience with S7-1200.
If the i-device addresses are outside the process image of the CPU, you must transfer all the data in one go (i.e. "consistently").
For this purpose you would use DPRD_DAT and DPWR_DAT system functions.
I just mention this for completeness sake. If you assign i-device addresses at the low end, you can just copy the addresses the normal way.
I have a micrologix 1200 with me, it communicates with pc with the help of Rs-232 Cable. My computer have Usb so i connect the usb to serial cable...
1,491
Hi ! Everybody ! Please..help me about communication between S7 1200 and inverter or any varispeed inverter had MODBUS support by module CM1241...
20
11,204
Hello everyone, M using micrologix 1200 and it is connected to net-aic using pm02 cable, then net-aic is connected to my laptop using pm02 and a...
3,965
Hi guys, I am so confused, I have my application tested and running perfect in my lap top, however running from PV shows a message that says not...
4,088
Hello let me explain my problem. I just got tossed into a somewhat complicated job because the person that normally does the writing is on...
3,837