Hi,

I have a S7-1200 and Beijer HMI. These are communicated with ethernet cable. I want to do that PLC communicate with another device via RS485. I know that S7-1200 needs additional module for RS485 communication. The HMI screen has a RS485 port. Is it possible to communicate PLC with other device using the HMI's RS485 port without the use of additional RS485 module? If possible, how can I do it ?

Sorry for my english.

Thanks.
 
s7 1200 modbus

this can be possible if your hmi can read from another device (modbus rtu for exemple) and copy data to PLC tags
 
What is the model of the Beijer HMI you are using? This will determine how you can communicate.
http://www.beijerelectronics.com/en/products/ix-hmi-solution

Regards,

Hi,

I use Beijer iX T7A HMI. HMI reads memory bits from plc. I want to reads these memory bits via RS485. For to do this, I define 2 controller on HMI. Controller1 is for Modbus and Controller2 is for S7-1200.

Here is the defined controller for Modbus.

WENnw7W.jpg



And here is the modbuss address.

J0mkSvW.jpg


I used Modbus Poll software for testing but I was not succesfull.
 

Similar Topics

can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
Replies
1
Views
409
Hi ! Everybody ! Please..help me about communication between S7 1200 and inverter or any varispeed inverter had MODBUS support by module CM1241...
Replies
20
Views
11,201
Is any one experience with s71200 any module support modbus TCP Communication?
Replies
2
Views
1,775
Hi! I have a S7-1200 1214C with RS232 Communication Module (CM1241) as Modbus Master I found an example of work with MODBUS in here...
Replies
0
Views
4,427
Hello everyone, M using micrologix 1200 and it is connected to net-aic using pm02 cable, then net-aic is connected to my laptop using pm02 and a...
Replies
15
Views
3,964
Back
Top Bottom