aqueousdan Member A Join Date Jan 2016 Location uk Posts 32 Feb 3, 2017 #1 Can anyone see why i am not getting an output on this? it is detecting a rising edge and saying that it is true but going any further to the output coil. I must be missing something obvious!
Can anyone see why i am not getting an output on this? it is detecting a rising edge and saying that it is true but going any further to the output coil. I must be missing something obvious!
RClem Lifetime Supporting Member Join Date Nov 2010 Location Pennsylvania Posts 110 Feb 3, 2017 #2 The output will only be true for one scan.
aqueousdan Member OP A Join Date Jan 2016 Location uk Posts 32 Feb 3, 2017 #3 If I put a set coil rather than a normal one though it still won't latch on.
RClem Lifetime Supporting Member Join Date Nov 2010 Location Pennsylvania Posts 110 Feb 3, 2017 #4 I simulated the posted logic with a set coil without issue, perhaps your output address is being referenced elsewhere?
I simulated the posted logic with a set coil without issue, perhaps your output address is being referenced elsewhere?
aqueousdan Member OP A Join Date Jan 2016 Location uk Posts 32 Feb 3, 2017 #5 Ok yes you were right, it was already being referenced. I redid my code and set and reset works perfectly. I cant see how to delete posts on this forum but i think i need to!
Ok yes you were right, it was already being referenced. I redid my code and set and reset works perfectly. I cant see how to delete posts on this forum but i think i need to!
RClem Lifetime Supporting Member Join Date Nov 2010 Location Pennsylvania Posts 110 Feb 3, 2017 #6 Good to see you found it. Rich