S7-1500 CPU and ET200M connection
EMENDOZA
May 2021
Binangonan Rizal
Dear Experts,
I have a question regarding the redundant S7-1500 CPU and ET200M connection.
Will ET200M IOs work on a redundant S7-1500 Controller using IM 153-4 PN IO HF, or do we need an IE/PB Link for the MRP ring network to link the ET200M Modules?
Because based on my attached proposed system architecture, it uses an ET200MP and ET200SP because both of them do support PN S2 Redundancy.
Our customer wants to replace the S7-300 CPU with a redundant S7-1500 CPU and retain the ET200M Remote IO Modules.
Thanks in advance
Most likely the existing ET200M will not work. If you use the TIA Selection Tool (available online or for download) the only ET200M modules allowed in a redundant system are on ProfiBus DP (IM153-2 or IM153-2 HF)
I've never seen them used in an S7-1500 system, but the HF ET200 PN interface module (6ES7153-4BA00-0XB0) says it supports S2 redundancy.
It isn't the full dual NIC redundancy that it can do with Profibus, but it's how they did PN redundancy with S7-400 until the new ET00SP HA came out.
Hi guys I was asked a question this weekend which I don’t know the answer. I hope you can help , we had an issue with a Siemens 1500 where the...
1,506
Hi I connected Cpu 1518(server OPC UA) to Hmi Factory talk se 11.0 with OPC UA, and I set Kepserver 6 (client OPC UA). I'm able to see in...
1,404
Old job-All AB... New Job-All Siemens... The idea is to take a new S7-1500 CPU and create a "ready to swap" backup for one of my machines. Had...
2,440
Hi all experts! I'm having a bit trouble with UDP communication with a CPU 1512SP-1 PN and a Kongsberg Seatex MRU 3. The MRU is set to output...
17
5,086
Hello, I’m developing a program and i found that my simulation works very well when i use CPU 1500 but when i use 1200 and i click download. A...