S7-300 Analog input module
recycled_mind
May 2007
Cebu, Philippines
118
Dear experts,
I would like to ask what should I configure with this Analog Input Module 6ES7 331-7KB02-0AB0. I have a 0-10V DC Analog signal coming from a sensor. I will input this to the first channel of 6ES7 331-7KB02-0AB0. I found out that in the HW Config Pull-down using Simatic Manager menu under E (voltage), I could not see 0-10V but +/- 10V. What should i select???
Please help, maybe I have overlooked some parts.
Thanks,
Alex
You can configure your analogue input/output while configuring your hardware. There are 3 possible configurations for analogue inputs and outputs
+/- 10 V
0 to 10 V
0 to 5 V
Configure your hardware to 0 to 10 V
I am a student. I can program PLC using LAD language using digital IO. But, I want to program using analog IO also. We have analog IO module with...
2,072
Hi All I am using 2 x analog cards on my rack and they are described as 12bit cards in there title. The manual suggests that the resolution can...
2,030
I need help sending an analog input (temperature) to an analog output (4-20ma)?
19
4,317
Hello, I have an: Analog input module SM 331; AI 8 x 12 bit;(6ES7331-7KF02-0AB0) I have 4 channels that are set up for 2-wire 4-20mA signals. HW...
7,194
This is my first Siemens PLC programming. I got a PLC 315-2DP with 1 DI, 1 DO and 1 AI modules. I have already configured the modules and then...
10,580