Hello mas-2000;
The addressing question is easy to answer: the HWConfig editor will set (allow you to select, if this is an analog module card) the addresses for the modules available. Generally analog addresses are in a range above 256 (digital addresses start at 0).
Each analog channel uses one 16-bit register representing the analog value; these values are not read into the process input/output table so they mare accessed through "peripheral" read/writes: inputs are PIW256, for example, outputs are PQW272.
Generally, an analog input card needs to be configured (software, in HWConfig, module properties; sometimes in hardware, if there are range modules to be selected and set). Details for each analog module in the S7-300 catalog is slightly different, and should be examined in the "S7-300 module data" manual (download it from the Siemens support website).
Moat modules will give you a numerical value between 0-27648 (unipoar signals) or +/- 27648 (bipolar signals) for the analog signal conneced to the channel; anything outside this range is over/underrange signal. The easiest way to handle them and scale them to engineering units is to use the integrated "SCALE" and "UNSCALE" functions, that you can find in the TI-S7 converting blocks library of the program editor of Step 7 (FC105 and FC106, respectively).
This is a very general view of using analog modules in Step 7; please indicate which model number yopu plan to use, what analog signal type you would like to connect (4-20 mA, =/- 5 V, PT100), so we may answer more precisely.
Hope this helps,
Daniel Chartier
I have a client who has asked for a pop-up for each of their analogs, which will display the alarm values. The values displayed in the pop-up...
2,553
hi i am using s7-300(CPU 313c). when i try to use FC106 unscale function, i can change IN manually but there is no effect on OUT. i wrote PQW752...
1,612
Hi guys, I have CPU S7-300-313C ( Cat No - 6ES7-313-5BE00-0AB0) DI24/DO16 and AI5/AO2. when I am trying to configure and use the AO channel PQW...
2,575
I am a student. I can program PLC using LAD language using digital IO. But, I want to program using analog IO also. We have analog IO module with...
2,087
Hi All I am using 2 x analog cards on my rack and they are described as 12bit cards in there title. The manual suggests that the resolution can...
2,045