S7 300 hardware configuration error
rj061991
May 2014
iligan city
75
Good Day!!
i am currently working on a bacon slicer machine here in the philippines.. iused tia portal for S7 300.. the machine was ok for almost 2 weeks... but suddenly the PLC turns into SF..i had monitored the plc online but it seems the plc hardware configuration goes error.. the CPU is ok but the I/O modules cannot be configured.. Is it possible that some of the I/O modules are defective??.. what should i DO??
Thank You
Jorem
Can you post your diagnostics?
What is your hardware? All local IO or remote?
Number 1 I would check is diagnostics. After that control voltage to your IO.
interesting thread, I also have the same question
im using an DI module, DO module, DO relay module, and Analog module..the program is functional.. i will upload the diagnostic and the image later.. but looks like this." STOP caused by I/O access error (OB not loaded or not possible, or no FRB)"
It might help to know exactly what you have..
OB122 might help you preventing the CPU to go in stop, but it will not solve your problem
i have attach the diagnostic buffer..and i just found out recently that one of the I/O module is defective..it cannot be configured..what safety precaution should i used to prevent the I/O modules from damage?
Hi, I got two questios: There are two slave devices(SEL-787) from which I should read data via MODBUS RTU. I checked SEL-787 manual and it says...
5,556
This is my first time using Siemens S7-300 PLC's and in this project I will be using a IM360 interface module to connect to 2 other racks using...
3,647
Hi, I'm using E300 as E3 Plus in emulation mode. E300 is Rockwell Automation's overload relay. But I get hardware fault when I enable Ground...
474
Hi, I have some remote IO connected to my S7-317-2 PN/DP system. I have 1 particular profinet remote IO which is not important to the system, and...
2,993
I'm setting up some E300's for an impending MCC upgrade, and I'm having some issues. I have the 193-EIOGP control modules, specifically...
1,336