s7 300 - power configuration
Sillver
Feb 2010
us
I'm working on a project where we will use a CPU 314C-2DP with 2 built in IO cards, 1 x SM331 AI, 2 x CP341 and 1 x CP343-1 Lean.
Will each module have a separate connection to the 24VDC supply or will the backplane bus power all the modules
For S7-300 there basically isnt any 'power configuration' to consider.
The CPU supplies 5V to the modules that attach directly to the right. Any combination of 8 modules (or 1 IM + 8 modules) you can imagine will be covered by the integral 5V power supply.
But some modules do demand a separate 24V supply, the CP343-1 do, and so do output cards.
ET200S is different. There you may have to calculate the power demand going through the backplane.
CP341 and CP343-1 Lean:
If I understand this correctly from documentation here http://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&objId=23523142&nodeid0=24285671&load=content&lang=en&siteid=cseus&aktprim=0&objaction=csview&extranet=standard&viewreg=WW
https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&objId=31397838&nodeid0=24284824&load=content&lang=en&siteid=cseus&aktprim=0&objaction=csview&extranet=standard&viewreg=WW
the CP341 and CP343-1 Lean require an external connection to the 24VDC. This external supply supplies the input and output circuits of the modules. The maximum current for the CP343-1 Lean will be 200mA and 100mA for the CP341 (for fuse sizes).
Digital I/O’s:
P276: http://cache.automation.siemens.com...0_cpu_31xc_and_cpu_31x_manual_en-US_en-US.pdf
The 24VDC shall be connected to 1L+, 1M to supply any DI’s connected on inputs 2-9, 24VDC connection over 2L+, 2M supplies DO’s connected to 22-29 and so on. The maximum current for the DI’s will be 50mA and 80mA for the DO’s (found here http://support.automation.siemens.c...objaction=csview&extranet=standard&viewreg=WW).
Did I get this right?
Dear all, My CPU312 is in RUN state, RUN and DC5V LED's are green. Still there is no input or output. CP341 (RS422/485) is also installed in a...
1,058
Hi, Could anyone please help me how to find or calculate the total power consumed by S7-300? so as to i can determine the UPS KVA rating. The...
1,268
My screen was damaged, so I ordered a new screen, I installed it. It says its booting. Then a fault comes up ' the CF card and the PP45 are...
1,121
Is there any reason I can't just use a regular 24VDC power supply to power an S7-300 series rack? From what I see, the only connections between...
3,792
Hi guys, I have a client wich keeps telling me to give him a solution to his problem. The problem is that he has an automation with a S7-300 and...