Hi!
I have never cross this kind of problem..
I have kind of working program on 315-2dp cpu.
Program has been working nearly 20 years like this, but now customer needs some changes.
But.. I can't go online, because plc program "hangs".
When setting PG to online, status bits on vat table are flashing randomly, and program status remain same state on every bit, even they should change status.. untill I switch PG to offline, then everything is ok again.
There is profibus network configured correctly, couple of VLT's, and couplers, all ok.
And MPI- bus configured to HMI. That works too.
No errors on diagnostic buffer, no error leds..
Resources are fine to my eye, 1 PG, 1 OP, 12 basics, and online: used 1 PG, 1OP, 0 basics.
And I have tested with 3 different PG's, and via MPI and Profibus. Same thing.
Only thing what I noticed, all programs are located in FB's, even they do not need to be FB's. And they are called in ob1 with UC..
Could that cause this problem?
Or what..
I have never cross this kind of problem..
I have kind of working program on 315-2dp cpu.
Program has been working nearly 20 years like this, but now customer needs some changes.
But.. I can't go online, because plc program "hangs".
When setting PG to online, status bits on vat table are flashing randomly, and program status remain same state on every bit, even they should change status.. untill I switch PG to offline, then everything is ok again.
There is profibus network configured correctly, couple of VLT's, and couplers, all ok.
And MPI- bus configured to HMI. That works too.
No errors on diagnostic buffer, no error leds..
Resources are fine to my eye, 1 PG, 1 OP, 12 basics, and online: used 1 PG, 1OP, 0 basics.
And I have tested with 3 different PG's, and via MPI and Profibus. Same thing.
Only thing what I noticed, all programs are located in FB's, even they do not need to be FB's. And they are called in ob1 with UC..
Could that cause this problem?
Or what..