S7-400 cpu led status
gdalianis
Jan 2008
Greece
17
does anyone knows what is the problem on an S7-400 cpu in case all the leds are constantly on (not blinking, I think in this case it that the cpu is defective).
Thank you
Check power supply.
I have a 6ES7 405-0RA00-0AA0 power unit and is this is power supplied by another psu 220 to 24V 37A. Both the leds 24V and 5V leds on the power unit is green as well as the 5V led on the IM 461-1 on the second rack. I also suspect that is possible that I have a problem on the initial power supply unit, is there a way to check it? Also at the power supply unis the indicator BAF is red with BA1F been orange. I tried to connect to the PLC. Allthought the step 7 is tryning to make the connection the cpu comes out grey at the end...
Please I am desperate to start the system and I still can not find what is source of the problem, any help would be highly aprecciated...
Before this occured, did you turn off the PLC? Then when you turn it on all LED is lit up and the BAF, and your program is not running anymore. I suspect that your PLC program was erased.
Change the PS battery and redownload the program. Make sure that before you turn off the PLC power supply, the BAF LED is not lit.
still no luck after replacing the batteries and eliminate the BAF on the power supply. The status of the leds of the cpu is the same and I can not connect to it with the pc.....
Try to reset the CPU with the MRES and the exercise with the RUN/STOP button. Leave the button in STOP position, and try to connect with the PC before you try to RUN.
Eventually also do a power cycle with the button kept in STOP.
Btw, is it a RAM or a Flash memory card sitting there?
Kalle
Kalle
Still no luck. I read the manual of the PLC to reset with MRES, but the led status at the CPU does not change according to the intructions of the manual. I can not connect to the CPU at all with my PC, even at the switch at stop. No additional card is installed at the CPU...
Hi All, I have a project that lets me control a Movimot drive via Profibus DP. A quick search on google learned me that a lot of information...
2,706
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
1,506
Dear Experts, We are currently in a project commissioning stage now of a Biomass Plant. The above mentioned CPU is used. 2 days ago, our load...
2,625
I want to replace the exisitng CPU card of our S7 plc with spare card of similar type. Is it as simple as just remove old one after switching off...
1,537
I have a defective S7-400 CPU 412 (6ES7 412-2XG00-0AB0) now can i replace it by CPU 414 (6ES7 414-2XG03-0AB0) without changing the program of the...
5,037