S7- CPU 314 analoge force

ahmed megahed

Member
Join Date
Nov 2010
Location
na
Posts
26
Hi gentlemen

Is it possible to force an analoge value in these CPU before 400
what i notice is i cannot write PIW128 in force table to force it ?

and also i tried to force IW128 instead of PIW128 is it the same or no ?
 
Analog inputs are normally placed in the periphery inputs (PIW instead of IW). So you cant just force these.

You probably have a scaling function, to convert the raw input to engineering values.
Add a simulate-bit as a condition (N.C. contact) before the scaling function. When you set the simulate-bit, the scaling isnt done. You can then manipulate the scaled value without it being updated by the scaling function.
 
Hi JesperMP
Thanks for your idea, it is OK.
But i need a clear answer is it possible to force analoge PIW by direct way like S7-400 or no ?
thanks
 
Hi JesperMP
Thanks for your idea, it is OK.
But i need a clear answer is it possible to force analoge PIW by direct way like S7-400 or no ?
thanks

It is not possible to force a PIW or to write to a PIW.

When the CPU reads a PIW, the value is accessed instantly from the input card via the backplane bus.

Dependant of the cpu type you can expand the process image area and thus put your analog(?) values in the IW area. The IW can then be overwritten with a T IW command.

Kalle
 

Similar Topics

Hello to All, Recently I install a CP343-1 Lean to communicate with a CPU 314 IFM, however I can't go online when I'm connected via CP343-1 Lean...
Replies
4
Views
1,672
Hi guys... been a very long time since I've posted... I have a few machines here from the Czech republic that came with siemens plcs in them...
Replies
4
Views
1,943
Hello Everyone! As the title suggests, i would like to know how to program a "First Scan Bit" in S7-300 PLC CPU314. I made a sequence with 3...
Replies
4
Views
3,164
Hello all, I have to solve how to repair a damaged CPU314PNDP by 230VAC, which came to 24VDC power supply line. Does anybody know, which...
Replies
5
Views
2,580
Good day I recently Changed a screen on a Machine from OP7 to KP400 Comfort using TIA portal v12. since the change the communication is a bit of...
Replies
6
Views
2,408
Back
Top Bottom