We are have speed problems with the following setup:
We are using UDP broadcasting for transmitting data to an MES Application on the server. We have configured 7 UDP Package Sends with 1500 bytes of data. In the beginning this setup worked well, but because of program additions we now see that the CPU Cycle time increased between 60 and 80ms.
When we log on the MES application, we can see that we receive data from a Package each aprox 400ms...
So we think that the cycle time * 7 Packages is the cause... that only one SEND is done per cycle... could this be correct ??
To speed things up we are thinking to replace the 317-PN/DP by a 319 CPU... ?
Can anyone give some advice how we can decrease the 400ms delay ?
Thanks in advace,
Kind regards,
Combo
It looks like you are sending the data out of the CP module. The communication would go significantly faster if it was sent directly out the integrated port of the CPU. This avoids using the backplane.
Ok
Ok...
So u think if we change the broadcast from CP to PN port that we gain speed ?
And change the cpu from 317 (60ms cycle time) to 319... wouldn't that be a fenomenal improvement ?
Thanks for your help,
Kind regards,
Gerry
The bottleneck is surely the 187.5 kpbs backplane. Start to use the PN port instead of the CP. To begin with it should not be necessary to change the CPU to a 319.
Changing to the onboard PN port can have as a sideeffect that the scan rate of OB1 increases. If that is not acceptable, you may have to change the CPU.
I am troubleshooting the setup of UDP broadcast receiving on a CP443-1 CP card. The telegrams appear in WireShark with IP 192.168.1.255 Port 7551...
2,292
Hi. Does anyone know how to use the Wago APP socket lilbrary functions for UDP broadcast? I have tried to use the fbUdpPacketClient function to...
2,355
Hello all, I am working on a project utilizing an s7-1200 cpu and Tia Portal v17. I currently have an external PCB with some sensors on it (and...
737
Hi PLCTalk Family, I am currently using S71200 for UDP communication in one of our projects. Recently due to the chip shortage looking out to...
1,293
Hi all, I was trying to communicate FX3GE PLC with KEPServer / Kepware via UDP protocol but did not succeed. Does anybody has any solution or...
1,065