S7300 Newbie question

In first, what are addresses of IO in your HW config? Second, did you install new empty PLC or PLC was in use before? Check Count field and disable count channels.
 
The problem is solved!!
It is pretty silly yet one of those untold siemens assumptions.

It was a wiring issue. If you look at the CPU 313C, it looks for DC+ on the input terminal but it also looks for DC+ on 1L+ terminal. I did not know that.. See, the LED comes on even if DC+ is not connected to 1L+ but the status is not displayed while monitoring..

Same issue with the outputs. If outputs are written, although it says a "true" status while monitoring the LED doesn't come on till DC+ and DC- are connected on 2L+ and 2M.

Thanks for all your help!!