Safe Heater Control Best Practice (preventing runaway)

When I have dealt with heater controllers that use SSRs, I have used a shunt trip breaker upstream of the SSR wired to a fault contact on the controller. If there is a PLC in the mix, I might also wire a PLC output to trip the breaker in case I detect anomalous temp signals.

The shunt trip breaker is more compact than a contactor in many cases and you need circuit protection anyway.

I like this idea, this would save panel space as well. Thank you for the input.
 

Similar Topics

Can somebody share the AutroSafe configuration Tool C4.11.4 Thank you
Replies
1
Views
114
I have a GuardLogix PLC with safety inputs of HMI, Estops, Light Curtains, and Gates. Is it considered safe for the safety program to monitor the...
Replies
11
Views
785
We have an existing VSD where a three phase circuit breaker feeds the drive, and two phases also tee off to a contactor, which is energised to...
Replies
12
Views
1,490
Hi, I'm trying to understand a couple of things with a feedback signals that are used in a SRP/CS that I'm working with. Quick disclaimer: I'm...
Replies
2
Views
536
Back
Top Bottom